Regarding the static measurements, I've been limiting my data to report only when the Inside and Outside temps are identical, typically most likely to be at the beginning of the day, when the car has not been operated for quite a few hours, and the temps have equalized. I don't know if that really makes any difference to the result, but it's one less variable to worry about.
When not running (static), the pressure equalizes throughout the entire system. This is true even if different parts of the system are at different temperatures. There is always a mixture of liquid and gaseous refrigerant (unless it is completely empty). The liquid refrigerant will collect wherever the coolest temperatures are. If the inside / outside temperatures are equal, then the chart gives you the expected saturation pressure. If the inside and outside temperatures are different, then you would use the lowest temperature to lookup the static pressure (because that is where the liquid Freon will be located). There will be times when the inside is cooler than the outside, and vice-versa depending on the scenario leading up to the measurement.
Bottom line - If the temperatures are both the same, the expected result is obvious. If they are different, then I will use the lower of the two when looking up the static pressure.