Really? At what point is this bonding occurring? Certainly not what I have come to expect.
Also
@The Gadgeteer may be interested. I know I beat this to death already, but I did another install today for a customer of a 6-50r receptacle in a garage (not for EV, but for a pottery kiln. Though if she or a future homeowner ever goes EV, this can also be used for L2 charging). Opportunity for a few clear photos of neutrals and grounds all mixed together on the bus bar, and also the bonding strip that connects these 2 bus bars. This is a correctly wired service panel.
This configuration would be INCORRECT for a sub-panel, however. Had this been a correctly wired sub panel instead of a main service panel, one bus bar would be all bare grounds, the 2nd bus bar would be all white neutrals, and the black bonding strip between the two bus bars would not be installed in the panel. This would isolate the grounds and neutrals from each other, as it should be in sub panels only.
Photo 1 just an overview of this very simple install. The outlet I installed today is immediately below the panel where I'm pointing, just for ease of wire fishing. Customer wanted least expensive location possible and this couldn't have been easier. In and out of the job in 1.5 hours start to finish, purchased $35 in materials including outlet, breaker, wire, box, faceplate, connectors, etc.
2nd 2 photos show mixed grounds and neutrals on both bus bars.
Last 2 photos show how the bonding strip connects the 2 bus bars together even though they're on opposite sides of the service panel from each other...making it one continuous bus bar (bonded).