Remember to consider the size of the 12V power cables that you will need. This area gets confusing quickly, because there are inverter ratings for peak load versus continuous load. Sometimes the 12V bus will be 13V to 14V, but just to quickly consider cables take 12V as an example.
Say you buy a 12V 2kW Xantrex inverter and plan to run 1500W continuous (or, at least have that capability). Assuming 100% conversion efficiency, you need to be able to supply 1500W/12V, or about 125A! (at 85% inverter efficiency, closer to 150A) That is the very problem with working at 12V instead of using the Traction battery more directly (not possible at present) where 1500W/365V(I forget the actual number for Clarity, just to show the idea) = a measly 4A!
Back to 12V (1,500W) for 125A continuous (still assuming 100% conversion efficiency), you should use a relatively large #2 cable, the proper crimp or bolt connectors, heavy Anderson type connectors, and proper fusing or a circuit breaker. It's very doable, just messy. I used a marine #2 cable with an outer loom covering for the plus cable on my gen 1 Volt (before I switched to a 2kW Honda generator). Also, study fuse open curves, because a 125A fuse, might open in minutes or longer for smaller overloads, and that might be enough time to damage the Clarity's DC-DC converter, or to overheat the wires. I was using BUSS MRC marine breakers, I think I had a 135A breaker in the Volt with the #2 marine cable. I don't remember the details, but the gen 1 Volt APM (DC-DC converter) was very robust. The gen 1 Volt battery was in the back behind the passenger seats, easy to get to under the hatchback, and it was easy to have an installed inverter out of the weather.
If you leave pigtails permanently installed (most practical), or some wiring of 125A circuit permanently installed in Clarity, some thought needs to go into crash protection. For example, the cable from the battery to the fuse or circuit breaker should be considered carefully both for length and vicinity to metal structural members, because a short to ground
before the fuse or breaker is a dead short 12V battery overload with great fire hazard.
It's definitely doable, but considering all the stuff to buy, build, and install, most folks (especially with a remote home where they can leave something there) should consider a 2kW - 3kW inverter generator. They are very reliable these days, run quietly for hours, and are easy to re-fill. Best part, no risk of damage to Clarity if something goes wrong.