If I understand your question correctly your asking has anyone put in a 30 amp/115 volt (NEMA TT-30 RV trailer receptacle) which would be a level one charger instead of a 240 volt/30 amp level 2 charger receptacle such as a NEMA 6-30 receptacle. The answer to your question on functionality is that the 115 volt 30 amp plug would be less efficient and take twice as long to charge as the 240 volt but it would be much quicker than a standard 12 amp charger.
From an installation standpoint both the 115 v/ 30amp and the 240 v/ 30 amp receptacle would require a dedicated 40 amp circuit, the same number of wires and wire size, so there would be no cost advantage to the lower voltage receptacle. For the TT-30 rv receptacle it would require 3-8 gauge wires, a ground, a neutral, and a hot. For a 6-30 240 volt dryer receptacle it would also require 3-8 gauge wires, a neutral and 2 hots. Given that is the case I would recommend installing the higher voltage receptacle which allows the quickest charging. In addition I would recommend upping the wire size to 6 gauge wire and a 50 amp receptacle and circuit breaker which would allow for future higher charging rates and the most options should they be needed.