Checking panel for capacity to add EVSE circuit

I never said that it meant that the load likely exceeded the rating of the main breaker.

You are correct. I misinterpreted what you said when you said “… your statement indicates that the sum is typically more which to me means likely to exceed”. It seemed obvious that if the sum was more (greater) that it would also exceed, no further explanation needed. So I assumed that you were implying that the load would likely exceed, which is not what you were implying. I realize now, that you chose the word “likely” because I chose the word “typically”. I did not use the word “always” for obvious reasons.

I apologize for the error and any confusion it may have caused.
 
Something to consider when using the calculating method is that if it passes the test it does so under current usage patterns. If usage patterns change, say for example that now with L2 and L1 charging capabilities in the garage, a homeowner decides to charge 2 cars simultaneously. We now have a load that was not part of the calculation that resulted in a passing score. Maybe grandma moves in and likes to keep a 1500W heater going in her room most of the time. It passed the test, however, there’s no proof that things won’t change. This test has flaws, particularly if there is guesswork involved in the calculations.

With the metering method, there is no proof that a maximum load condition was ever measured. Again, it passed the test, however, measuring the load for a few seconds out of every hour, doesn’t show us what was happening the other 59 minutes and 30 seconds of each hour. This test is probably the most flawed of the three.

The sum of individual breakers method is the most likely to guarantee a service panel will not become overloaded, provided that the sum is less than the main. However, that situation rarely exists.

To be clear, I am not suggesting that the tests are useless or should be disregarded. A homeowner who is attempting to decide whether or not a circuit can be added to a panel should be aware that passing a NEC test, does not offer proof that the panel will not become overloaded at some point.
 
S

The sum of individual breakers method is the most likely to guarantee a service panel will not become overloaded, provided that the sum is less than the main. However, that situation rarely exists.
Please chime in anyone if their panel has less breaker values than their main breaker panel

I had a full on machine shop running on a 60 amp sub panel
On that sub panel I had:
2 rotary 3 phase converters which operated
2 3 hp CNC mills
1 3hp manual mill
1 5 hp cutoff saw
1 1 hp saw
1 5 hp lathe
1 2 hp tumbler

single phase loads
1kw lights
air compressor
2 ton AC
2 drill presses

had as many as 4 guys working

started popping the breaker

so if you do that and then add an EV

YOu still won't have a problem
 