Robert_Alabama
Well-Known Member
The last posts on this got way off the general topic of the thread, so I thought I'd start a new thread. Hopefully I can do a better job of at least introducing the topic and having some constructive discussion. If I fail again, I'll probably just give up, but I tried... and for what it is worth, I am trying to be helpful.
I'll give a specific example of a panel in my house:
I have a panel that has a 200A main breaker, three 240V breakers, and 16 120V breakers. The sum of amperage of the 240V breakers is 130A and the sum of the amperage of the 16 120V breakers is 265A.
From what I understand for NEC here, there are 3 accepted methods to show the panel loading doesn't exceed the 200A capability.
1) add all amperages of the breakers (assume 120V load is balanced). This would be 130A plus 0.5*265A = 262.5A. So this method will not work to show the panel is not overloaded.
2) put a ammeter on each of the two hot legs feeding the panel and record amps at 15 min intervals for 1 year (or a minimum of one month in the peak load season) - this is not practical for most of us to do, and I'd probably only do it as a last resort. With this method, you would take the highest amp reading and multiply by 1.25 to get the panel loading.
3) add up all the loads on each of the circuits and multiply by 1.25 for a continuous rating. For this panel:
240V breaker #1 (30A) Dryer - 5400W or 22.5A
240V breaker #2 (60A) 5T A/C - 26.3 RLA for compressor and .97 FLA for fan - total 27.3 A
240V breaker #3 (40A) 4T A/C - 18.5 RLA for compressor and .93 FLA for fan - total 19.5 A
120V breaker #1 (20A) Refrigerator - 3.3A from nameplate
120V breaker #2 (20A) Washing Machine - 10A from nameplate
120V breaker #3 (20A) Kitchen island outlets - Hardly ever used - approximate as 3A
120V breaker #4 (20A) Utility room plugs - never used - approximate as 2 A
120V breaker #5 (15A) Attic squirrel cage motor for A/C air handler - 6A
120V breaker #6 (15A) Guest bedroom lights - LED lights - 1A
120V breaker #7 (15A) Guest bathroom lights and plugs - 12A (assume small hair dryer)
120V breaker #8 (15A) Child bedroom lights - LED - 1A
120V breaker #9 (15A) Bonus room - not used - LED lights 1A
120V breaker #10 (15A) Garage lights and plugs- LED lights - 12A (just in case 120V evse is plugged in)
120V breaker #11 (15A) Foyer lights and plugs - LED lights -1A
120V breaker #12 (15A) Child bedroom lights - LED lights - 1A
120V breaker #13 (15A) Office lights and plugs - computer and printer - LED lights - 5A
120V breaker #14 (15A) Attic lights - LED lights 1A
120V breaker #15 (15A) Playroom - no TV or media- LED lights - 1A
120V breaker #16 (20A) Porch fans - LED lights - 2A
This sums to 69.3 A on the 240V breakers and 62.3A at 120V (31.15A at 240 if balanced)
This total is 69.3A + 31.15A = 100.45 possible continuous load
add 25% for continuous load rating of panel = 100.45A *1.25 = 125.56A
If I wanted to add a 60A circuit in this panel, I would pretty much just have enough room as 125.56A + 60A = 185.56A. I made a lot of approximations on the 120V circuits and assumed perfectly balanced load which is likely not right, especially since all these circuits were planned with incandescent lighting load when they were attempted to be balanced, so I would feel better leaving a few amps to spare in the calculation. If I messed any of this up, I apologize as again, I am not a licensed electrician. I simply wanted to state that there is a process for determining panel loading which generally assumes all connected load is simultaneously on (with the exception of heaters and A/C - take the larger of these loads). It is not acceptable to add a circuit and say that I won't charge the car when the range/dryer/air conditioner is on and that as such the panel loading is ok. Again, if I am off base on this, I apologize in advance and I'll accept any criticism thrown my way...
I'll give a specific example of a panel in my house:
I have a panel that has a 200A main breaker, three 240V breakers, and 16 120V breakers. The sum of amperage of the 240V breakers is 130A and the sum of the amperage of the 16 120V breakers is 265A.
From what I understand for NEC here, there are 3 accepted methods to show the panel loading doesn't exceed the 200A capability.
1) add all amperages of the breakers (assume 120V load is balanced). This would be 130A plus 0.5*265A = 262.5A. So this method will not work to show the panel is not overloaded.
2) put a ammeter on each of the two hot legs feeding the panel and record amps at 15 min intervals for 1 year (or a minimum of one month in the peak load season) - this is not practical for most of us to do, and I'd probably only do it as a last resort. With this method, you would take the highest amp reading and multiply by 1.25 to get the panel loading.
3) add up all the loads on each of the circuits and multiply by 1.25 for a continuous rating. For this panel:
240V breaker #1 (30A) Dryer - 5400W or 22.5A
240V breaker #2 (60A) 5T A/C - 26.3 RLA for compressor and .97 FLA for fan - total 27.3 A
240V breaker #3 (40A) 4T A/C - 18.5 RLA for compressor and .93 FLA for fan - total 19.5 A
120V breaker #1 (20A) Refrigerator - 3.3A from nameplate
120V breaker #2 (20A) Washing Machine - 10A from nameplate
120V breaker #3 (20A) Kitchen island outlets - Hardly ever used - approximate as 3A
120V breaker #4 (20A) Utility room plugs - never used - approximate as 2 A
120V breaker #5 (15A) Attic squirrel cage motor for A/C air handler - 6A
120V breaker #6 (15A) Guest bedroom lights - LED lights - 1A
120V breaker #7 (15A) Guest bathroom lights and plugs - 12A (assume small hair dryer)
120V breaker #8 (15A) Child bedroom lights - LED - 1A
120V breaker #9 (15A) Bonus room - not used - LED lights 1A
120V breaker #10 (15A) Garage lights and plugs- LED lights - 12A (just in case 120V evse is plugged in)
120V breaker #11 (15A) Foyer lights and plugs - LED lights -1A
120V breaker #12 (15A) Child bedroom lights - LED lights - 1A
120V breaker #13 (15A) Office lights and plugs - computer and printer - LED lights - 5A
120V breaker #14 (15A) Attic lights - LED lights 1A
120V breaker #15 (15A) Playroom - no TV or media- LED lights - 1A
120V breaker #16 (20A) Porch fans - LED lights - 2A
This sums to 69.3 A on the 240V breakers and 62.3A at 120V (31.15A at 240 if balanced)
This total is 69.3A + 31.15A = 100.45 possible continuous load
add 25% for continuous load rating of panel = 100.45A *1.25 = 125.56A
If I wanted to add a 60A circuit in this panel, I would pretty much just have enough room as 125.56A + 60A = 185.56A. I made a lot of approximations on the 120V circuits and assumed perfectly balanced load which is likely not right, especially since all these circuits were planned with incandescent lighting load when they were attempted to be balanced, so I would feel better leaving a few amps to spare in the calculation. If I messed any of this up, I apologize as again, I am not a licensed electrician. I simply wanted to state that there is a process for determining panel loading which generally assumes all connected load is simultaneously on (with the exception of heaters and A/C - take the larger of these loads). It is not acceptable to add a circuit and say that I won't charge the car when the range/dryer/air conditioner is on and that as such the panel loading is ok. Again, if I am off base on this, I apologize in advance and I'll accept any criticism thrown my way...
Last edited: