With temperatures below 10 F (-12 C), the house heater, a high efficiency Lennox SLP98UH110XV60C stopped working around 10 AM. Calls to the local Lennox dealers revealed they are booked up until after Christmas. A grim Christmas future.
The installation manual was with the unit and I soon found the error code, E228 meant the pressure sensor indicates a blocked flue or air intake pipe:
Since our pine trees have been shedding needles, I got on the roof but no problem found:
I have a fear of heights and did this solo.
The pressure sensor was failing. YouTube videos confirmed the diagnosis.
Using a jumper, the failure occurs during the "calibration" startup:
At this lower fan speed, the heating is reduced. This allows the furnace to operate just a little faster than the heat loss from the outside cold. I've set the thermostat to a high temperature to extend the house warming. So far, it is working. But eventually the furnace will warm up the house enough to turn off heating.
After a time delay, the calibration cycle will restart but fail because of the static jumper. Calibration must start with the switch OPEN and then close during the combustion fan speed step. Disconnect when the fan goes to idle and back ON when it steps up.
LATER THAT NIGHT
At 5:30 AM, we just had a power outage. The automatic emergency generator came on 30-45 seconds later and I restarted the furnace.
Lights, power, and heat …. neat.
- Calibration starts - pressure switch OPEN
- Combustion and flue fan starts a stepped speed up - pressure switch eventually CLOSE during speed steps. So I applied a jumper to substitute for the failing switch
- Flue fan backs off to initial speed - pressure switch OPEN, remove jumper
- Flue fan speeds up to the step when jumper installed
- Furnace continues to operate adding ~8 F per hour. The TV room measured 40 F at 8:00 PM and now shows 65 F at 11:30 PM and heater is still running.
LATER THAT NIGHT