ADVICE NEEDED: fish smell from house circuit board when car charges

Discussion in 'Hyundai Kona Electric' started by Hillel Soberman, Oct 19, 2022.

To remove this ad click here.

  1. Hillel Soberman

    Hillel Soberman New Member

    Car: 2021 Kona EV
    Car Charger: hardwired ChargePoint Home Flex
    Circuit Board: dedicated 60 Amp Breaker
    Unit was set to charge at 50 Amp

    Car issue: (number of months ago) car check EV warning light went on and stayed on.
    • I took it to my local Hyundai dealership, and they made a software adjustment to limit my charging to 80%.
    • There is no recall on my VIN to replace the battery.
    • The dealership deemed the car safe to drive with the limited range.

    Now I discovered a new problem.
    • Really, it has been going on for many months, but only recently did I connect the dots to realize that this is an electrical issue (and that it can be potentially dangerous).
    • I do not know if my new problem is related to the EV warning light issue, and I do not know if the timing of the two happened at the same time.

    New problem: when I plug in my car to charge at home (ChargePoint charger), after about 10 to 15 minutes, my basement smells like fish.
    • After much trial and error, I realized that the smell was coming from my electrical breaker board for my house and that the smell only occurred when I was charging my vehicle at home.

    I called an electrician. He does not have extensive experience with electric cars.
    • The 60 amp breaker burnt completely black!!!! He felt that we were lucky that we did not have a house fire.
    • He replaced the burnt breaker with a brand new one and the fish smell came again.
    • I had the ChargePoint unit replaced (it was under warranty) and tried the new unit at slower speeds (less than 50 Amp). Unfortunately, the dreaded smell returned.
    The 60 amp breaker runs hot when the car charges. No other breakers in my house breaker board show any damage.

    Currently: I have the breaker off and can no longer charge the car at home.

    Anyone experience something similar or have any ideas? I am really in need of some problem solving advice.

    PLEASE HELP?!?!?

    Thanks in advance and keep smiling :)
     
  2. To remove this ad click here.

  3. From my experience and what I have read, the Kona EV on a L2 EVSE is limited to 32 amps or 7.4 kw. That is what my Grizzl-e EVSE is set to and I have not smelled any fish. My circuit breaker is 50amps.
     
  4. You've certainly provided more info (other than location) than many other requests for help on this forum but the fish issue really does seem like an electrical problem in your home. It's not possible for the Kona to pull more than 32-ish amps and it's little different from any other load in the house.

    I'm sure @electriceddy will be along at any moment to provide more enlightened commentary but the electrician needs to check the wiring and neutral-ground bonding more carefully. But as best as I'm aware it's the charger that cares more about those points than the car.

    You can reduce the Kona's current at the dash using either the "minimum" or "reduced" station charging settings, if that would help narrow down the problem. You can also set the ChargePoint to 16 amps which does essentially the same thing.
     
  5. That smell *could* indicate some small rodent has expired in a wall cavity. Heavy current draw generates heat, which could warm the remains.
     
  6. Nahhh... OP already said the circuit breaker on the switch board was burnt out. It's an electrical problem, not a biological one.
     
  7. To remove this ad click here.

  8. I have to say my Wallbox wall box gets quite warm and the region around the 40 amp breaker gets warm too even though it's only pulling 32amps. I'm presuming this is normal. The wiring for my setup was specifically run from the meter and sized for high amperage workshop and EV charging.
    It does sound like the OP has a wiring issue.
     
  9. Pastera

    Pastera New Member

    What is the brand of your panel?
    What do the cables look like at the breaker?
    Electrician shouldn't care what it connected to the load at all - the issue is in the panel. If there was an overcurrent causing excessive heat that's the breaker's job to prevent.

    It sounds like the bus bar in your panel is bad and is overheating the breaker due to I^2R losses (it doesn't take a lot of resistance to burn up a connection at 32 amps
     
    electriceddy likes this.
  10. teslarati97

    teslarati97 Well-Known Member

    Coincidentally, Munro Live just posted a video regarding Home Charging Installation Risks.

     
    Clay and navguy12 like this.
  11. Certainly that could be what's happened, heating at the circuit breaker screw termination or the buss connection. The OP's charger is hardwired so there's no low-quality NEMA outlet to worry about. It does seem surprising that these components are out on the market yet can't support well under their rated load.
     
    navguy12 likes this.
  12. To remove this ad click here.

  13. hobbit

    hobbit Well-Known Member

    The spot(s) on the panel bus bars should be checked out too. If the old breaker was arcing there due
    to a loose clip where it connects, the bus bar itself might be burnt and distorted. A new breaker
    might only get screwed up in short order by that poor feed contact. Moving the breaker to a different
    slot might be an interim fix.

    _H*
     
    Clay and Pastera like this.
  14. When I think about the issues raised by Munro with the NEMA outlet and circuit breaker, it's clear to me that the problem may arise where a set screw clamp is made directly on stranded wires, or the set screw is accompanied by a plate to effect a parallel-acting clamp. The wire strands are ductile and need a more circumferential clamp that applies an even radial compressive force on the bundle. The set screw works onto a small area and will not be able to maintain tension over a long period, as in years. A parallel clamp partly relies on the strands not unwinding under pressure. Neither have much springiness to help maintain contact.
    [​IMG]
    Much is said about the plug and receptacle contact resistance increasing with repeated use but I suspect problems in that area are less common. Those parts are designed specifically to maintain continuous contact pressure and the materials are selected to have suitable properties.

    The EV itself has no such issues because all connections are machine-crimped circumferentially to controlled dimensions. Related plug and socket connections are similarly made to high standards, and despite sitting for years undisturbed, don't exhibit issues. Industry is full of electrical connection examples that work just fine.

    This could be more a failure of the relevant domestic N. American electrical standards, product design and quality control, that EVs have simply brought to the surface due to the essentially-continuous loading.

    Tests I did some time ago when I found one 10A AU/NZ extension cord plug getting warmer than the others indicated the problem was from a poor quality crimp buried inside the molded plug. These were made of material that was probably too thin, not crimped in a controlled manner and then soldered as well, which alters the material characteristics. Heat generated by the resistance of the soldered joint can't easily escape through the plastic so travels both up the copper wire and down the plug pin. But the latter has only a physically small contact to the receptacle and can't conduct much heat out. Heat going up the wire adds to the warming already present due to wire resistance, so the cord gets warmer near the plug.
    I measured the actual pin and socket electrical resistance and found no problems with that, all were 4.4 milliohm.

    IMG_2192.jpeg
    upload_2022-10-22_14-52-28.jpeg
     
    navguy12 and electriceddy like this.
  15. All wires in N.A. larger than #10 AWG are stranded typically 7 strands for building wire, any competent electrician will use a quality flat bladed screwdriver to tighten the connection first (better yet a hex Allen key), then move the wire around to seat it properly, then re-tighten the termination to achieve a permanent solid bond. By permanent, I mean to say under continuous (as well as intermittent loads where the conductor expands and contracts due to current requirements) will last ~10 years or more before a re-tightening is required. I typically carry a specific set of screwdrivers strictly used for larger wire terminations.
    I always use the back of my hand to "measure" temperature conditions within the electrical enclosure, before opening and inspecting, for good reasons I will not expand on at this time.
    The author of this thread has (as suggested above post #7) has not given any information to:
    Age of the electrical panel
    Main service capacity (including overall calculated load)
    Type and sizes of conductors
    etc
    If I had to speculate (which I hate to do- even with pictures) is a bus bar issue, possibly a bolted copper bus that has exceeded the 40 year life expectancy under normal residential conditions where the screws that bond the bars have loosened and over heating has been generated.
    The video makes a reference to Hubbell and Bryant type termination devices (ie a 14-50 receptacle) which are indeed industrial quality and really the best quality, ones I use for large loads. I also notice some of the conductors were of Aluminum, really bad idea, even using an antioxidant such as Penatox. Using the methods indicated above using copper, I have never had any issues.
    I could talk (and show pictures) for hours of the horror shows I have encountered over the years, how little it really takes to start an electrical fire, and in opposite situations, how much equipment can surprisingly actually withstand, without causing one, but I will refrain at this time.
     
    Andy Murray, navguy12 and Pastera like this.
  16. See, OP just needed an experienced electrician!

    The Munro video is interesting because as usual Sandy talks the most but knows the least, and manages to continually present a facial expression that could sink a ship. I'm glad that the two other guys at least had a high level of technical knowledge, if not that much specific to the subject discussed.

    My impression of the evidence presented is that none of those are likely to have actually started a house fire. They all failed in the intended manner, even though it looks gruesome.
     
    navguy12 likes this.
  17. Rob G

    Rob G New Member

    Usually overheating electrical connectors create an acrid small of burning plastics.

    I had an annoying "fish" smell when a poor electrical lighting connector was overheating in the ceiling and charring some cellulose type of roof insulation.
    I looked up the specifications of the old flaked cellulose and it had originally been treated with fire retardant and blown into the ceiling cavity, swamping electrical cables. Apparently this was a cheap method in Australia and worked well for about 6 months :(
     
    Last edited: Oct 22, 2022
  18. What is the New Zealand house wiring standard supply?
     
  19. hobbit

    hobbit Well-Known Member

    I never trust pre-molded plug/socket heads on high-current extension cables. I always lop them off
    and install real ones [or multi-outlet boxes with spec-grade outlets] for anything I'm serious about.

    If you tighten a connection onto copper and go back a while later to apply a steady torque onto the
    screw and hold that for a few seconds, the screw *will* move more in that direction as the copper
    settles into its new constraint. Very good to pay attention to in things like breaker panels.

    _H*
     
    navguy12 likes this.
  20. 230VAC 50Hz single phase at often just 60A with neutral bonded to ground at the main panel. All very simple and a wall-mounted home charger would be hard-wired, mostly to minimise cost. We don't normally have the customary fitment of a heavy-duty outlet in the garage and kitchen as common in N.A. Electric ranges can have a 32A receptacle but electric clothes dryers just run off a normal 10A outlet.
     
  21. Jim1960

    Jim1960 Member

    I would suggest that there is something wrong with the ground wire either in the house electrical panel, or in the connection to your EV charger (the ChargePoint). The fried breaker strongly indicates that there is a grounding problem specific to the charger circuit. (And yes, I know it isn't technically an "EV charger", but I can't remember the alternate word.)
     
  22. I think the OP has probably had their problem fixed and has disappeared into the ether.
     
    navguy12 likes this.
  23. navguy12

    navguy12 Well-Known Member

    EVSE ;)
     